- ~4 p! a0 l4 s7 p1 t9 l; Y做了几年美标,这个问题貌似我能回复。
& D, C0 i8 h, b: w: E3 e7 z1598标准也是没有说明class2的线可以裸露在建筑内部哦,倒是8750这个标准有条款7.4.1.2,但这个线也是有限制的。这条款ITS那边是接受的;我问过UL,但是没有收到他们的确认回复邮件。$ B3 G; x8 X5 t9 t, {2 ?
7.4.1.2:Power limited circuit wiring that is intended to be routed within a building structure shall be of a
4 W6 a M$ A6 r; Ytype suitable for application (e.g. CL2, CL2P, CL3, CL3P, CL3R, CM, CMP, CMR, or PLTC) and in
% y- g X9 r/ F1 {& N* ~accordance with Article 725 of the National Electrical Code (NEC), ANSI/NFPA 70 |
|