Portable Socket-outlets
* M- G/ l. T0 Q9 K2 {; WTesting Requirements for the Temperature Rise Test according to DIN VDE 0620-1
0 c5 c% i, C9 l ^. k# i5 A5 wWith immediate effect, cords having a cross sectional area of 1,0 mm² are not allowed for portable socket-outlets with VDE or VDE GS Mark. Tests performed by the VDE Institute have shown, that portable socket-outlets having cords of this cross sectional area always exceed the allowed temperature limits according to DIN VDE 0298-300. The VDE Institute has informed his customers about this fact by the following letter: 16:50 23.02.2009
x/ o/ G3 x( j5 @' s* D$ ~$ d) m: U- i" [
For portable socket-outlets – consisting of socket-outlet, cord and plug – the temperature rise test according to DIN VDE 0620-1:04-2005, differing from table 20, has to be applied at a testing current of 20A on all parts of the product (socket-outlet, cord and plug) – irrespective of the cross sectional area, see also EK1 decision No. 393-08.$ u0 G& H3 k3 {. V t
7 \ |4 l c5 K& W
Therefore it is necessary, to supplement the testing requirements according to the safety-relevant gaps found in the standard.* O+ o7 O; @, b2 }
3 Y. M, ^1 a2 Q' Q p1 |8 JThis means, that e. g. a temperature rise test on portable socket-outlets according to DIN VDE 0620-1:04-2005 at a testing current of 20A is necessary irrespective of the cross sectional area. If for this product, a cord having a cross sectional area of 1,0 mm² is used, a temperature rise measurement directly on the cord is also involved.
/ `5 v* m; N( e* h3 w+ B% V
/ p) i$ D7 V0 E4 _2 J5 iBased on the tests performed so far on 1,0 mm² cords the allowed temperature limits according to DIN VDE 0298-300 (VDE 0298 Part 300):2004 tables 4A or 4B are always exceeded. For this reason it is no longer possible to certify products having a cross sectional area of 1,0 mm².
2 w: Z3 }" L3 U2 i7 Y) T' [, `, `) n, o2 r6 _
The current marks approvals will be adjusted, i. e. the cross sectional area of 1,0 mm² will be deleted from the certificates.6 M* {4 G, @! R: |4 ?7 X1 i
; L, e/ M- G1 u1 i: i& hHence from now on with immediate effect, cords having a cross sectional area of 1,0 mm² are not allowed for portable socket-outlets with VDE or VDE GS Mark. This fact will be published on our homepage in the internet.
m& J, C. J5 m! L8 {6 l) i+ G9 D* n4 M. H0 z, J
A respective update of the appendices to the relevant marks approval certificates will be sent to you shortly. |
|