Portable Socket-outlets & _ W7 q! H9 Z* k7 o* w
Testing Requirements for the Temperature Rise Test according to DIN VDE 0620-1( j3 P# r, A! q5 a: x* M
With immediate effect, cords having a cross sectional area of 1,0 mm² are not allowed for portable socket-outlets with VDE or VDE GS Mark. Tests performed by the VDE Institute have shown, that portable socket-outlets having cords of this cross sectional area always exceed the allowed temperature limits according to DIN VDE 0298-300. The VDE Institute has informed his customers about this fact by the following letter: 16:50 23.02.2009& A1 N, i. Z9 t% S- {
" l% H# M& f0 P! s0 ~9 B7 M4 J
For portable socket-outlets – consisting of socket-outlet, cord and plug – the temperature rise test according to DIN VDE 0620-1:04-2005, differing from table 20, has to be applied at a testing current of 20A on all parts of the product (socket-outlet, cord and plug) – irrespective of the cross sectional area, see also EK1 decision No. 393-08.* X% z. d+ G+ @, n
; r) K' d+ M% S* e( }. [
Therefore it is necessary, to supplement the testing requirements according to the safety-relevant gaps found in the standard.7 v: m$ C* W, h" F1 C) I/ {
2 I; n! v8 D* [: z' w; x! ~This means, that e. g. a temperature rise test on portable socket-outlets according to DIN VDE 0620-1:04-2005 at a testing current of 20A is necessary irrespective of the cross sectional area. If for this product, a cord having a cross sectional area of 1,0 mm² is used, a temperature rise measurement directly on the cord is also involved.
% @+ w, b& \+ K3 o7 K: ?. B+ g* Q& h$ o6 u, y
Based on the tests performed so far on 1,0 mm² cords the allowed temperature limits according to DIN VDE 0298-300 (VDE 0298 Part 300):2004 tables 4A or 4B are always exceeded. For this reason it is no longer possible to certify products having a cross sectional area of 1,0 mm².8 M/ p* `' N9 e& ^% T
/ G( `7 H8 K8 f/ _
The current marks approvals will be adjusted, i. e. the cross sectional area of 1,0 mm² will be deleted from the certificates.
( B3 R7 y) ^5 p' F* ?5 Y8 }& |
0 x) c+ Y+ L. Q# T7 jHence from now on with immediate effect, cords having a cross sectional area of 1,0 mm² are not allowed for portable socket-outlets with VDE or VDE GS Mark. This fact will be published on our homepage in the internet.9 L2 ]6 c |# j& l, ]1 e: p
& O) \9 u* P6 N, V9 sA respective update of the appendices to the relevant marks approval certificates will be sent to you shortly. |
|