插头的内外高压测试问题
插头做好后,需做高压测试(Hi-pot test),IEC-60884标准中只规定一个2000V(1、所有极连一起与本体之间;2、每一极与本体的其它极之间),一般都会把这个2000V理解成内压,外压在标准里没有说明,而一般会根据实际情况,将外压定为4000V。请问以上的做法有没有什么不当的地方。 2000V 不是很清楚呢,好像都对呢
4000V是不考虑接地的情况下进行的
而2000V是考虑接地下进行的。 外压怎么没有说明呢?60884的17.1.2里面明确描述了测试的位置 弄个中英文对照的:
17.1 The insulation resistance is measured with a d.c. voltage of approximately 500 V, the measurement
being made 1 min after application of the voltage.
用約500V 直流電壓測量絕緣電阻,施加電壓後1 分鐘進行測量。
The insulation resistance shall be not less than 5 MΩ.
絕緣電阻不得超過5MΩ。
17.1.1 For socket-outlets, the insulation resistance is measured consecutively:
對於插座應依次在如下部位測量絕緣電阻︰
a) between all poles connected together and the body, the measurement being made with
a plug in engagement;
在所有連接在一起的極與本體之間,測量時插入插頭;
b) between each pole in turn and all others, these being connected to the body with a plug
in engagement;
依次在每個極與所有其它極之間,測量時所有其它極要在插頭處於插合的情況下
連接到本體上;
c) between any metal enclosure and metal foil in contact with the inner surface of its
insulating linings, if any;
在金屬外殼與金屬箔之間,金屬箔與可能有的絕緣襯墊的內表面接觸;
NOTE 1 This test is only made if an insulating lining is necessary to provide insulation.
注︰該項試驗僅在必須絕緣襯墊提供絕緣功能的條件下才進行。
d) between any metal part of the cord anchorage, including clamping screws, and earthing
terminal(s) or earthing contact(s), if any, of portable socket-outlets;
在線夾內的每個金屬部件(包括夾緊螺絲)與移動式插座的接地端子或接地措施
(若有)之間;
e) between any metal part of the cord anchorage of portable socket-outlets and a metal rod
of the maximum diameter of the flexible cable inserted in its place (see table 17).
在移動式插座的線夾內的每個金屬部件與一根直徑等於軟線最大直徑的、且插入
軟線的接線位置的金屬桿之間(見表17)。
The term "body" used in a) and b) includes all accessible metal parts, metal frames
supporting the base of flush-type socket-outlets, metal foil in contact with the outer surface
of accessible external parts of insulating material, fixing screws of bases or covers and
coverplates, external assembly screws, earthing terminals or earthing contacts.
上述a)和b)條中所述的“本體"包括可觸及金屬部件、支撐暗裝插座底座的金屬框
架、與可觸及外部絕緣件的外表面接觸的金屬箔、底座或帽蓋和蓋板的緊固螺絲、
外部裝配螺絲、接地端子或接地措施。
NOTE 2 Measurements c), d) and e) are not made on non-rewirable portable socket-outlets.
注2︰不可拆線移動式插座不進行上述c)、d)和e)的測量;
NOTE 3 While wrapping the metal foil round the outer surface or placing it in contact with the inner surface of parts
of insulating material, it is pressed against holes or grooves, without any appreciable force, by means of a
straight unjointed test finger test probe 11 of IEC 61032.
注3︰用金屬箔包覆絕緣件的外表面或貼在絕緣件的內表面上時,應將金屬箔輕輕壓入孔洞或凹陷中,壓入時使用
直線無關節的IEC 61032 探棒11 的試驗指。
17.1.2 For plugs, the insulation resistance is measured consecutively
對於插頭應依次在如下部位測量絕緣電阻︰
a) between all poles connected together and the body;
在所有連接在一起的極與本體之間;
b) between each pole in turn and all others, these being connected to the body;
依次在每個極與所有其它極之間,測量時所有其它極應連接到本體上;
c) between any metal part of the cord anchorage, including clamping screws, and earthing
terminal(s) or earthing contact(s), if any;
在線夾內的每個金屬部件(包括夾緊螺絲)與接地端子或接地觸點(若有)之間;
d) between any metal part of the cord anchorage and a metal rod of the maximum diameter
of the flexible cable inserted in its place (see table 17).
在線夾內的每個金屬部件與一根直徑等於軟線最大直徑的、且插入軟線的接線位
置的金屬桿之間(見表17)。
The term "body" used in a) and b) includes accessible metal parts, external assembly
screws, earthing terminals, earthing contacts and a metal foil in contact with the outer
surface of accessible external parts of insulating material, other than the engagement face.
上述a)和b)條中所述的“本體"包括可觸及金屬部件、外部裝配螺絲、接地端子、
接地插銷以及與可觸及外部絕緣件的外表面(插合面除外)接觸的金屬箔。
NOTE 1 Measurements c) and d) are not made on non-rewirable plugs.
注1︰不可拆線插頭不進行上述c) 和 d)的測量;
NOTE 2 While wrapping the metal foil round the outer surface or placing it in contact with the inner surface of parts
of insulating material, it is pressed against holes or grooves, without any appreciable force, by means of a
straight unjointed test finger test probe 11 of IEC 61032.
注2︰用金屬箔包覆絕緣件的外表面或貼在絕緣件的內表面上時,應將金屬箔輕輕壓入孔洞或凹陷中,壓入時使用
直線無關節的IEC 61032 探棒11 的試驗指。
17.2 A voltage of substantially sine-wave form, having a frequency of 50 Hz or 60 Hz, is applied for 1 min
between the parts indicated in 17.1.
在17.1 條所述的部件之間施加一個頻率為50Hz 或60Hz 近似正弦波形的試驗電壓1 分鐘。
The test voltage shall be as follows:
試驗電壓大小如下︰
− 1250 V for accessories having a rated voltage up to and including 130 V;
對於額定電壓130V 及以下的插接裝置,1250V;
− 2000 V for accessories having a rated voltage exceeding 130 V.
對於額定電壓130V 以上的插接裝置,2000V。
Initially, not more than half the prescribed voltage is applied, then it is raised rapidly to the full value.
開始是施加不足規定值一半的電壓,然後迅速升壓直至完全達到規定值。
No flashover or breakdown shall occur during the test.
試驗期間不得出現閃絡或擊穿。
NOTE 1 The high-voltage transformer used for the test should be so designed that, when the output terminals are
short-circuited after the output voltage has been adjusted to the appropriate test voltage, the output current is at
least 200 mA.
注1︰試驗時使用的高壓變壓器必須具有這樣的特性︰將輸出電壓調至相應的試驗電壓後使輸出端子短路,這時輸出電流應
至少為200mA。
NOTE 2 The overcurrent relay should not trip when the output current is less than 100 mA.
注2︰輸出電流小於100mA 時過電流繼電器不得動作。
NOTE 3 Care is taken that the r.m.s. value of the test voltage applied is measured within ±3 %.
注3︰注意測量施加的電壓的均方根值時精確到±3%。
NOTE 4 Glow discharges without drop in the voltage are neglected.
注4︰無電壓降的輝光放電忽略不計。 版主提供的双语标准很详尽。可否这样理解:
a) between all poles connected together and the body;
在所有連接在一起的極與本體之間;
这条规定的是外压;
b) between each pole in turn and all others, these being connected to the body;
依次在每個極與所有其它極之間,測量時所有其它極應連接到本體上;
这条规定的是内压;
而标准中只是提到了以额定电压130V为界限的2000V和1250V,如果上面内外压的理解正确的话,似乎内外压的值都是一样的,要么都是1250V,要么都是2000V。这样对吗? 不过VDE审厂员告诉我们将外压设定在家2200-2500V,后面其他国家审厂员来我司审厂都没投述此问题,因为此前我司将外压调试到达4000-4500V,VDE审厂员说这样是破坏性测试,而不合格。 作为例行试验,打耐压不是电压越高越好,过高的电压会使绝缘受损,从而加速其失效。适可而止。 我这里去年也被VDE和SONY质问过(我司耐压打的2400V/2S).
相关讨论点:
VDE的Plug的要求(VDE0620-1-2010的第17.2项):
U≤130V,测试用AC 1250V 时间1min
U>130V,测试用AC 2000V 时间1min
(U为额定电压, 测试电压有效值的公差为3%)
VDE的Connector的要求(VDE 0625-2002的15.2项)
芯线间(L与E,N与E间)耐压为2000V±60V,时间为60S±5S
芯线与本体间耐压为4000V±60V,时间为60S±5S
(测试电压有效值的公差为3%)
但是,在工厂检查项的指引里:
PM 375 E-2010-04-08的3.2.1项要求:
对于自动记时的设备,测试时间可以允许缩减为2s(不低于1S);
2000V±10%,
或者4000V峰值电压,3次脉冲,时间每次不低于1S;
分别施加于L极与E极间,N极与E极间(L与N极要连接)
如果加严测试会引起将产品击穿的话,
那我们如果按照VDE 0620-1-210的要求来做,使用2000V的有效值,有效值公差为3%,即2000V±60V来测试,时间1分钟,
这样的话,设备的峰值电压又应该是多少呢?
为什么VDE0620-2010里是2000V±3%,而PM 375 E又要求为2000V±10%呢?这个不是范围更大吗?
为什么不直接将标准里的公差写成±10%?
如果加严测试说不被允许的话,那VDE0625既然参照IEC60320-1-2007的话,在连接器的耐压测试为什么不按照IEC60320-1-2007的第15.3项:芯线间的耐压为1500V±60V,时间60s±5s来做,而在PM 375 E-2010-04-08的3.2.1项里要加严测试呢?
从绝缘厚度和绝缘强度来说,插头和连接器的在耐压击穿的角度上,同样厚的绝缘,难道耐压能力会有不同吗?
如果说因为电压偏高而导致产品被击穿而未被发现的导致产品流出到市场的话,
那么还可能涉及到仪器本身的点检是否有效的问题了.
可以说是挑战仪器校正的准确性的问题了.
仪器校正的耐压输出和有效范围,以及电压的稳定性难道不测试的吗?
=============================
通过调整,中间改了一段时间2000V±200V/2S
现在又被VDE同意了,改回用3000+100V-0V/2s外高压。
以上,仅供参考。 见过标准,没做过具体的试验,谢谢楼主分享