caochun 发表于 2014-5-22 18:34

求各位幫助 ,英文內容何意思 ?

I recently purchased an 8-kw portable generator.I was extremely surprised to find that the manufacturer included an extension cord with a male 250-V, 30-Amp male cord cap to supply four 125-V, 15 Amp outlets on the load side of the cord.This creates serious problems.We now have 125-V, 15-Amp outlets protected at 30-Amps.Additionally, these cordsets are readily available and the use of such a cord completely negates the new GFCI requirements in 445.20.Does UL list such a product?

H-RH 发表于 2014-5-22 23:46

本帖最后由 H-RH 于 2014-5-23 01:59 编辑

笔者内文意思大致如下:"买了一部 8kW 发电机, 附带了一条伸延电线, 但这款电线违反了最新美国条例, 究竟这个产品是否有 UL 认证?"

首先, 内文所指违反之条例是 NEC 445.20, 即 NFPA 70 之 Section 445.20! 很不幸, 笔者所指的 NFPA 70 Section 445.20 是 2014 版之新增, 安规网内之 2011 版是没有的!
上网找了半天, 445.20内文如下:
445.20 Ground-Fault Circuit Interrupter Protection for Receptacles on 15 kW or Smaller, Portable Generators. All 125-volt, single-phase, 15-and 20 ampere receptacle outlets, that are a part of a 15 kW or smaller, portable generator, either shall have ground fault circuit interrupter protection for personnel integral to the generator or receptacle, or shall not be available for use when the 125/250 volt locking-type receptacle is in use. If the generator does not have a 125/250 volt locking-type receptacle, this requirement shall not apply.
由于笔者没有清楚说明是伸延电线什么不符合条例, 但本人估计是没有 GFCI (Ground Fault Circuit Interrupter)


另有一个小插曲, 曾经有生产商上诉要把条文改成 :
445.20 Ground-Fault Circuit Interrupter Protection for Receptacles on 15 kW or Smaller, Portable Generators. All 125-volt, single-phase, 15-and 20 ampere receptacle outlets, that are a part of a 15 kW or smaller, portable generator, either shall have ground fault circuit interrupter protection for personnel integral to the generator or receptacle, or shall not be available for use when the 125/250 volt locking-type receptacle is in use. If the generator does not have a 125/250 volt locking-type receptacle or was manufactured or remanufactured prior to January 1, 2015, this requirement shall not apply.
即在 Jan 01, 2015 前生产之发电机可以豁免, 但最终上诉被驳回!

H-RH 发表于 2014-5-23 01:53

还有一个疑点, 条例中只是说发电机那些 Receptacle outlet 需要有 GFCI 保护功能, 没有指明伸延电线(extension cord)要有 GFCI.
假设发电机已经内置了 GFCI, 即使用了伸延线也自然有保护功能!

madeinnp 发表于 2014-5-23 08:26

貌似客人最担心的是一个250V/30A 的code 要供4个125V/15A的输出。所以他在250V/30A的code那边加了一个125V/15A的保护。

麦子-tmac 发表于 2014-5-23 08:42

客户两点疑问啊,第一是你用30A的输入线头,但是你的插座是15A的,不匹配,所以客户把15A的插座换成了30A的。第二点就是你这样的线违反了GFCI要求

H-RH 发表于 2014-5-23 10:36

本帖最后由 H-RH 于 2014-5-23 11:58 编辑

麦子-tmac 发表于 2014-5-23 08:42 static/image/common/back.gif
客户两点疑问啊,第一是你用30A的输入线头,但是你的插座是15A的,不匹配,所以客户把15A的插座换成了30A的 ...
其实这段我也有想过:
"an extension cord with a male 250-V, 30-Amp male cord cap to supply four 125-V, 15 Amp outlets on the load side of the cord. "
笔者没有清楚描述这条 extension cord, 这个 250V 是什么意思呢?
发电机输出 250V? 如果这样, 伸延线后之插座怎可能变成 125V?
发电机输出 125V? 如果这样, 125x30 达不到 8KW?

如果这条电缐插头之所谓 250V 笔者是指那种 2 phase 4线 (NEMA 14-50 : L1, L2, N, GND) L1-N/L2-N各125V, 那便较为合理! 2 组 125V 各 30A, 输出是4组125V 各15A!

caochun 发表于 2014-5-23 17:00

產品圖片如附件 ,不明白為何不符合 ,

H-RH 发表于 2014-5-23 17:49

本帖最后由 H-RH 于 2014-5-23 18:19 编辑

图片中的插头看不清楚, 是否 NEMA L14-30P?

caochun 发表于 2014-5-23 18:41

是的 , L14-30P

caochun 发表于 2014-5-23 18:49

插頭電流 30A 是大於尾部 15A ,電壓 如125 V 等於 尾部的電壓 。怎麼就不符合了 ?
页: [1]
查看完整版本: 求各位幫助 ,英文內容何意思 ?