DSH 761 Measurement point of temperature rise in non-rewirable socket-outlets
http://decisions.iecee.org/icons/ecblank.gif DSH 761
Measurement point of temperature rise in non-rewirable socket-outlets
19
60884-1(ed.3);am1
Question:
The standard reads: "Socket-outlets are tested using a test plug with brass pins having the minimum specified dimensions. … For this test, the temperature rise is measured on the terminals."
Two representative pictures of possible measuring points (A = termination of contact tube; B = contact tube itself) in non-rewirable socket-outlets are shown below. Which point should the temperature rise be measured?
Decision:
The temperature rise shall be measured on the termination of the contact tube (point A).