* ~" Y: I* t! Z! P | New glow wire test requirments (650 C) for parts close to contacts
- K. P7 l. E# v( F9 u* a/ K" { | Clause 7.1.1.1 of IEC 60947-1 Clause 21.1.5 of IEC 61058-18 i. x4 P# b m# j6 k3 t" S7 t
| 61058-1(ed.3) & 60947-1(ed.4)) i' R' P8 [, F+ e" I$ U2 d
|
! t5 S! S; \2 q+ e" sStandard(s)- (year and edition):# f4 x0 y! ?9 L9 d7 Y
IEC 60947-1:2004 IEC 61058-1:2000
* H' a1 l; g, l& mSub clause(s):+ J n. \/ c b- o5 M( a p0 S
Clause 7.1.1.1 of IEC 60947-1 Clause 21.1.5 of IEC 61058-1. z" P: L: V' ^1 W$ G! W1 c; a, O
Sheet n°: @" ^8 Y, r; _
DSH 5932 t0 M7 m) Q0 F) n4 d
Subject:/ u( p- k8 u9 o) [6 J
New glow wire test requirements (650 °C) for parts close to contacts
( G' E& f1 ]/ R- G0 g! H& g0 JKey words:9 R( J% c% s1 t( L+ V5 D+ x# g4 G. \( i
- glow wire. |8 H* m! c e& J4 Z$ f" W9 G+ O" W
Decision approved by the 44th CTL meeting 2007
- f3 v4 T0 I0 R5 ~) T RQuestion:0 @( ^! v; S v z* l5 p3 ^9 @* x
Due to the new requirements of 60947-1:2004, parts close to contacts are subject to glow wire test performed at temperature of 650 °C. Is a glow wire test necessary for the green part (figure 1) or isn’t a glow wire test required for this part?5 [% w8 n$ P1 h6 `) ?
Decision:
y' ^6 h6 X# h! u, f( [Although the green part (figure 1) of this switch is mechanically separated from the contact element, the glow wire test should be done with 650 °C. During normal operation, the switching element and the contact element are mounted together. Due to this fact and the relatively large amount of material, a test should be done.: L1 c" h; X; z9 E, s4 c