| PDSH 892
# n9 Z4 h: w/ e* L
6 |" u N: W% S | Earthing in luminaire system
U6 c" k& U z2 k( a; [# `- c2 S | 7.2.1
J5 `% r2 s6 ? | 60598-1(ed.3);am1 & 60598-1(ed.4);am1 & 60598-1(ed.5) & 60598-1(ed.6);am1 & 60598-1(ed.7)" p1 J' b Z. G/ j7 o( h6 R
| 3 E( N, R+ L; T: e* S
Standard(s):
2 |4 x1 k" d( `IEC 60598-1 All editions# `- l4 v& c- v* i L$ F
Subclause(s): 7.2.13 n1 I; o# o9 W$ z8 L; h
No. Year DSH 0892 20106 ?2 J: U7 D3 L! U" i
Category: LITE Developed by: ETF5 OSM/LUM
" ]/ }" D. ~+ |9 v4 m+ r$ q# CSubject:3 Y: Q9 Z" w$ q) h# ?9 H) D- [
Earthing in luminaire system& T5 j; D( O- o- n
Key words: b3 X( o3 c! U$ W* J/ [! [+ V
- Metal body8 K7 V* Y; y8 X8 l
- Each luminaire1 X, H9 V( U5 b1 Q9 N3 Z& u! S1 n* z
- Fixed installation
3 x( s1 w A# b* zApproved at the 49th CTL Plenary Meeting, in 2012& d) }7 E. d( |0 S N
Question:
" T" V+ O/ L: j1 e2 V( mIn a luminaire system:" \4 {) g) h, ~* K
a) Can the metal body provide earth continuity instead of copper conductor?
L& ~/ P& C6 M* V" R9 Ab) Can the earth continuity be connected in series (feed through) as part of the fixed installation?
9 L. e3 ?9 x: `Decision:3 u2 [- ? Z1 q# n
a) Not acceptable.
% }' O. w _8 H" A, D6 Q7 xb) Not acceptable, each luminaire must be directly earthed.
3 I# G6 |: V* r3 B& _; Q5 L3 W( W# H7 L' x7 X. e# y$ V' s: z