安规网

标题: 关于耐压测试和Breakdown. [打印本页]

作者: 大侠风清扬    时间: 2008-12-10 16:45
标题: 关于耐压测试和Breakdown.
[原创]关于耐压测试和Breakdown.% l% a2 P' S% G5 c6 @5 _

4 `% M. ~/ V8 p5 u; X& S. i' [1.    本帖主要讨论耐压测试中如何判断Breakdown(主要是固体绝缘).% A) B1 _9 l3 j, n/ m- R/ q) j
2.    引用标准 IEC 60243-1:1998, IEC 60664-1:2007, IEC 60335-1: 2001+A1:2004+A2:2006,+ T, U% b5 b" s. w# A  g8 O
IEC 61180-1:1992 和IEC 61180-2:1994.
" |8 M: f* m7 M. r对于IEC 60335-1, 我想这是一本大家都比较熟悉的标准了, 就不多解释了. 下面介绍一下另外几本本标准.+ [) w- M- r. n5 x
IEC 61180-1 High-voltage test techniques for low-voltage equipment) N  w7 C4 C; m1 Q
Part 1: Definitions, test and procedure requirement9 o: D/ H" R* Q1 B4 o  M  |9 Y% S
这本标准主要给出了一些定义测试环境,测试电压的要求和测试程序.
% V& x/ h6 b+ P" `' `* _: `9 w; xIEC 61180-2 High-voltage test techniques for low-voltage equipment - Part 2: Test equipment
- H; R$ w5 c9 u% u* @& j2 E这个是测试设备的要求0 I& B  g" I, r# W+ f, \/ N
IEC 60664-1 Insulation coordination for equipment within low-voltage systems – Part 1:
0 p. C$ g+ p% E3 O8 l- [Principles, requirements and tests
; G: ?# R* a- M6 o5 N这本标准主要是讲固体绝缘特性之间的关系, 并给各个TC(技术委员会)制定标准给出了指导性的说明.
, M6 z+ R, v/ h: E% X' q9 C' Y3 |" ~$ {& X5 L+ s" R
scope如下:
1 U/ u4 E, h& q2 [' I1 Scope and object0 f/ P. R+ H+ U2 V5 O1 j
This part of IEC 60664 deals with insulation coordination for equipment within low-voltage' ?: v1 {' a% K, l0 G1 C7 b
systems. It applies to equipment for use up to 2 000 m above sea level having a rated voltage
4 v/ c1 i1 ~0 T1 ~up to a.c. 1 000 V with rated frequencies up to 30 kHz, or a rated voltage up to d.c. 1 500 V.! O( B/ U" I) Z5 n# \4 g
It specifies the requirements for clearances, creepage distances and solid insulation for4 Y- X/ y) D8 @" ^( z* n; V" u$ j
equipment based upon their performance criteria. It includes methods of electric testing with2 U+ ~- R+ V7 N; Q: {9 x- e( V
respect to insulation coordination.
9 J* K9 ]5 n: rThe minimum clearances specified in this standard do not apply where ionized gases occur.% m: p/ f, f+ ?' `0 Y& a
Special requirements for such situations may be specified at the discretion of the relevant) |+ k+ Q: v  F
technical committee.
: S9 L5 i0 J9 e% `! @This standard does not deal with distances
4 g( F0 |5 m6 _% e7 k( V" |% i. S– through liquid insulation,
9 t  ?2 l  }; I* |; M– through gases other than air,
5 P' k- f" C2 J# K8 S, h( p– through compressed air.! S4 \' i) q6 o, W3 y  H
NOTE 1 Insulation coordination for equipment within low-voltage systems with rated frequencies above 30 kHz is
. R2 |+ ]; C* @$ D1 Igiven in IEC 60664-4.
6 I( D5 n  ?/ x; [. `( xNOTE 2 Higher voltages may exist in internal circuits of the equipment.
" r. R- T5 Y" m  T1 XNOTE 3 Guidance for dimensioning for altitudes exceeding 2 000 m is given in Table A.2.. w& l1 h, L/ L+ g  s$ B
The object of this basic safety standard is to guide technical committees responsible for different equipment in order to rationalize their requirements so that insulation coordination is achieved.
! y( a' [: ~1 u; t* VIt provides the information necessary to give guidance to technical committees when specifying clearances in air, creepage distances and solid insulation for equipment./ y2 J. B6 e( D9 G; Y( p" Z
Care should be taken to see that manufacturers and technical committees are responsible for application of the requirements, as specified in this basic safety publication, or make reference to it, where necessary, in standards for equipment within their scope.
) K. V" P- {: G  @3 q9 uIn the case of missing specified values for clearances, creepage distances and requirements for solid insulation in the relevant product standards, or even missing standards, this standard is applicable.
% p7 G" p( n+ v" `& _$ n' }* |$ s2 ]2 _
IEC 60243-1:1998 Electrical strength of insulating materials –Test methods –Part 1:Tests at power frequencies
& H. r4 P% k- B: _这本标准讲的是关于在市电频率下进行耐压测试方法.& l6 J% f' J: i3 P% `. k
Scope 如下:+ ]8 y3 y, k. ]/ r& _5 v' q5 C
1.1 Scope
* j0 B8 u: \6 O: @This part of IEC 60243 gives methods of test for the determination of the short-time electric strength of solid insulating materials at power frequencies, that is, those between 48 Hz and 62 Hz. It does not consider the testing of liquids and gases, although these are specified and used as impregnants or surrounding media for the solid insulating materials being tested.
+ }3 p  ?3 }, f8 X- W8 O: Y" T; SNOTE – Methods for the determination of breakdown voltages along the surfaces of solid insulating materials are3 f: u% V  W* c6 Z) d' ]
included! ^: `2 G- h& R! Q
8 J! {& v4 L% Z* t2 t4 e
3.    几种耐压测试.  b. [6 n# F$ A  k0 U
IEC 60664-1中讲述了爬电距离, 电气间隙,固体绝缘和耐压测试之间的关系,其中主要使用的是脉冲电压(impulse voltage dielectric test),直流电压, 交流电压高频电压.而IEC 60335-1 主要使用的是交流电压来进行耐压测试的. 本帖的讨论主要以交流电压为主.$ ], C  L1 {5 \- x3 c
% ~0 b7 X* |- F: e  d
4.    耐压测试结果的判断3 w$ k$ ?1 P5 H
以IEC 60335-1的16.3条款为例, 耐压测试的判断结果的方式只有一个breakdown.
' ?& N  x) i3 \& y, W" a( p原文最后一句如下:$ ^0 ]; y- i; v& j& H, A) o$ p
“No breakdown shall occur during the test.”
! K, h+ X! Q9 n- a% g除了breakdown没有其他方式没有其他方式可以用来判断结果.
9 I+ r' I4 @- H" D% v  h3 k
+ [0 ]4 K! `$ ^/ Q2 n5.    关于breakdown的定义.
% ~4 o- B/ I* y) \# lIEC 60335-1, IEC 61180-1 和IEC 61180-2中没有给出这个定义, 但是IEC 60243-1 和IEC 60664-1分别给出了定义. 对于跨标准引用定义是不合适的,但是在家电,灯具,工具,多媒体的各个IEC标准中都没有这个定义, 那么合适的定义只有从其参考的标准来看了.. |( Q$ z+ D: a8 `- O7 K6 Z
IEC 60335-1 的条款2中将IEC 60664-1作为参考标准的.(不过是1992版的)
5 K8 p! Y% t/ @* F' E而IEC 60664-1 中的定义是& L3 K+ {& L5 R" d3 y3 c/ b3 E" N
electrical breakdown
: H4 P1 }( w' |6 [2 {, Sfailure of insulation under electric stress when the discharge completely bridges the insulation, thus reducing the voltage between the electrodes almost to zero2 o( K) z( x, w4 n6 X6 N1 Y5 ~0 y
除此之外没有更进一步的说明.
% \" s5 K9 m1 t+ _7 ]3 q4 _IEC 60243-1 作为IEC 60664-1的参考标准列入了条款2. 并且也给出了定义:
$ r$ _% i0 h$ T( g% [( T! i7 helectric breakdown0 B$ U' T: {! E% s
severe loss of the insulating properties of test specimens while exposed to electric stress, which causes the current in the test circuit to operate an appropriate circuit-breaker! t- {) L; z' [- @: [5 j3 ^
NOTE – Breakdown is often caused by partial discharges in the gas or liquid medium surrounding the test specimen and the electrodes which puncture the specimen beyond the periphery of the smaller electrode (or of both
" n2 }2 J4 c* Ielectrodes, if of equal diameter).
, ^; G) b6 V& r这个两个定义很相似, IEC 60243-1中指出了绝缘击穿造成circuit breaker 动作, 但是这个circuit breaker 是不是很多网友所说的100mA动作的脱扣器呢? IEC 61180-2关于测试设备的要求中完全没有提到这个circuit breaker.关于这个100mA动作的脱扣器我稍后再解释,各位网友可以查一下自己的耐压测试设备, 一般情况这个100mA的脱扣器是一个通过电流传感动作的继电器.: m/ _: M1 A6 f3 |. M( H" K
IEC 60243-1中除了定义之外,在第10章给出了更详细的解释.
" Z' A) J( }+ s) {- S10 Criterion of breakdown
" d/ l+ c- z6 R. z5 g: d7 H10.1 Electric breakdown is accompanied by an increase of current flowing in the circuit and by a decrease of voltage across the specimen. The increased current may trip a circuit-breaker or blow a fuse. However, tripping of a circuit-breaker may sometimes be influenced by flashover, specimen charging current, leakage or partial discharge currents, equipment magnetizing current or malfunctioning. It is therefore essential that the circuit-breaker is well co-ordinated with the characteristics of the test equipment and the material under test, otherwise the circuit breaker may operate without breakdown of the specimen, or fail to operate when breakdown has occurred and thus not provide a positive criterion of breakdown. Even under the best conditions, premature breakdowns in the ambient medium may occur, and observations shall be made to detect them during tests. If breakdowns in the ambient medium are observed, they shall be reported.
* G* m% u0 U9 P) N9 ENOTE – For materials for which the sensitivity of the fault-detecting circuit is of particular significance, the standard for that material should so specify.
+ ~- D6 `9 \+ B' G6 U# Q从这里可以看出circuit breaker动作和breakdown也没有直接的关系.5 Y. p: @: p  i- t* E

* |% t1 T' f$ }9 [10.2 Where tests are made perpendicularly to the surface of a material, there is usually no doubt when breakdown has occurred and subsequent visual inspection readily shows the actual breakdown channel, whether this is filled with carbon or not.
2 Q9 f; S7 M$ {Breakdown还需要找到哪个地方击穿了.! T( [) t8 x% ]4 W7 }

# O/ ~. e# A" {+ E$ X2 D% {$ S( R10.3 If in tests parallel to the surface it is required that failure by puncture and failure across the surface are differentiated (see 4.2), this can be done by examination of the specimen or in some cases by reapplying a voltage less than that of the first apparent breakdown. A convenient practice that has been found is the reapplication of half the breakdown voltage, followed by increasing the voltage until failure is reached by the same procedure as in the first test.3 W3 Y, F" j) c" j$ H
找不到哪个地方击穿了,用这个方法再次确认.! j  O/ r+ e# W
虽然无法确认这个脱扣器和这个circuit breaker 是不是同一个东西但是这个装置的动作是不能用来判定breakdown的.(如果有其他网友有这方面的资料,欢迎提出来一起讨论)
3 e2 ^' w- _7 N8 g# t$ T查了一下, 没有额定电流为100mA的断路器, (断路器上标的30mA是对漏电流的), 这个断路器应该是固定布线上的
+ r, b" J  H7 [# m  B% A  P) {7 `, t
6.    关于100mA的问题6 x+ b$ x1 N' k) q/ u# J
关于这个100mA的问题也有很多人在讨论. 从IEC 60335-1的条款13.3来看.$ `3 k; P- @8 O* J; u2 c4 Y
“The high-voltage source used for the test is to be capable of supplying a short circuit current Is between the output terminals after the output voltage has been adjusted to the appropriate test voltage. The overload release of the circuit is not to be operated by any current below the tripping current Ir. The values of Is and Ir are given in Table 5 for various high-voltage sources.”3 ^1 a/ [% }6 \/ M
Table 5中指出对于4000V以下的, Is为200mA, Ir为100mA.其中200mA是以high-voltage sources(也即是耐压仪)的容量为 800VA来定的(IEC 61180-2要求的是100mA).100mA这里写得很清楚, 这个是过载装置的动作电流.而且也可以设置得比100mA高.这个装置的设定很明显是用来保护设备的.
+ f6 `  Z  v: a/ ]3 R- z: Q- w6 M$ a9 c- V5 z$ [
关于routine test中动作电流的设定可以参考IEC 60664-1中条款6.1.5.2
$ D0 q  V) ~/ P, ?$ O- k6.1.5.2 Sampling and routine tests: l) L7 y1 D8 ?3 m7 ]: G5 C6 V
Sampling tests and routine tests are intended to ensure production quality. It is the responsibility of the relevant technical committee, and in particular of the manufacturer, to specify these tests. They shall be carried out with the waveforms and voltage levels such that faults are detected without causing damage to the equipment (solid insulation or components).: C/ F( I' B3 t3 J6 J
Technical committees specifying sampling and routine tests shall in no case specify test voltages higher than those required for type testing.* d" C. Y) A: T/ u$ {6 r5 L
所以你可以认为这个电流的设定是用来避免耐压击穿直接损坏产品(有的产品可是很贵的)
. Y+ ~9 J- W+ I# ]9 u0 \' E' k! l" i0 F$ _- @. I/ \& y7 M
这里再讲一下,耐压测试中泄漏电流和击穿的关系:
7 W; R; Y4 d1 _9 Y; b
/ y& Q. B6 H, p如果耐压击穿则泄漏电流必然很大。(很大意味则超过100mA,也就很多人说的那个限值)。泄漏电流超过100mA,不一定击穿。
1 |8 V7 X' N7 a" |) z1 \- l也就是说,泄漏电流大不是击穿的充分条件。3 T( j4 i, G- ?1 z7 z
为了证明A+B不等于C,下面给出一个反例,也就是说泄漏超过100mA,耐压仪报警也不一定是击穿。$ R; x7 |, u, S0 [+ [: S+ Y; c

% `1 r$ {- A) H* y( e8 j根据60950的
* _7 K/ k) X2 u' F3 G0 E/ G1 _1.5.9.4 Bridging of basic insulation by a VDR
7 y9 r* C- N' T# }  WIt is permitted to bridge BASIC INSULATION by a VDR provided that one side of the VDR is earthed in accordance with 2.6.1 a).4 P$ `5 w/ E) {6 V

. _0 u; E( k& u7 m, i! [4 i" i也就是说VDR是可以跨接在基本绝缘两侧的。如果我们进行针对基本绝缘的耐压测试,假设基本绝缘耐压1500V,VDR型号为S14K385MOV,测试中耐压仪报警并指示泄漏电流超过100mA,这时我们需要检验是不是真正击穿,重新对这个VDR测试耐压但是耐压调到500V,如果没有击穿说明VDR只是在耐压测试过程中动作了并没有击穿。
+ I: j& K& s# T, m. C! V" R如果500V依然报警,说明VDR在先前测试中击穿。
- m5 `8 f7 E4 e; k* r& p
) i; w, M3 ], {' M) B) h回帖的讨论希望有标准和实验数据作为参考..
( I( P" w6 _  d3 {$ o3 U7 v2 N( J" f1 i. `$ `
原创, 版权所有不得转载!!
6 `: U, _* h" v2 V: c* t. y; }

作者: caballo3157    时间: 2008-12-11 20:50
楼主主要引用的IEC标准。
8 W7 v  w! ?3 d- Y6 f: QE文困难,又想了解其内容的可参考:  W4 \: y1 C8 R2 i3 h
GB1408   (IEC 60243)+ M3 U4 H/ P, J5 |" t9 V! a/ ?
GB/T 16935 (IEC 60664)7 b) J' L1 x  @. v- H3 a1 u0 S4 M
GB/T 17627 (IEC 61180)- P3 [. F7 X1 E8 P* [
GB4706.1  (iEC 60335-1)
作者: 4sea    时间: 2008-12-20 22:37
高手啊, 受教了!3 Z! }$ n  s4 Y- X. {
目前, 我所接触过的实验室都是以耐压测试时设备的过流触发电流100mA作为breakdown的判定依据的. 我想, 估计这是因为IEC60664-1中的定义中, 对breakdown的判断目前没有很统一的可实际操作的方式, 而100mA是一个比较直观量化的判断标准, 大家就将其作为一个默认的方式了.& M' Q: H. c; V
2 n5 S4 v8 g, ^/ H% J8 X
在实际生产中, 安全标准上routine test通常只有规定耐压电压的一半, 但大部分工厂都将其测试电压提高到规定耐压值稍高一些, 同时将测试时间减短, 不知道LZ有没有此类变通方法的出处?
. e( K4 q% N/ }6 J$ t' E* L0 d
% m0 K: e9 \( C4 J+ y2 R  l  o9 a另外, 很多标准有提到Flashover, 不知LZ能否也给大家讲讲其定义和判断方式呢?
作者: lixuf1    时间: 2008-12-22 20:29
当人体流过100mA以上电流时,人就会呼吸困难,心脏停跳
作者: ajay    时间: 2009-1-4 13:45
对于击穿问题,目前还是没有很好的解析。
作者: xieyanyi    时间: 2009-1-6 20:46
IEC 60335-1通用标准,要结合具体产品标准。13.3和16.3章测试的电压是不一样的。
作者: mangala    时间: 2009-1-23 10:31
要理解耐压测试中的Breakdown(绝缘击穿), 就必须了解几个概念.
0 V7 R' R' `( o( ]# }9 Z首先, 我们来看看标准是如何定义绝缘击穿的.
: e7 [8 r3 V& Z% a; pGB4943(IEC60950) 5.2.2中描述到"当由于加上试验电压而引起的电流以失控的方式迅速增大,即绝缘无法限制电流时, 则认为已发生绝缘击穿. 电晕放电或单次瞬间闪络不认为是绝缘击穿." 从物理角度来理解, 就是施加到绝缘材料上的电压迅速降到接近0V, 而电流达到无穷大, 我们则认为该绝缘出现击穿了.7 Y! r$ R) X! j2 A# l" w: }7 A/ C
第二, 绝缘击穿(Breakdown)与短路(Short)的区别;
* E( m1 A+ K: h% X3 Y; Y) M  P, j短路(short)是指电源输出端由导线直接闭合成回路. 对于耐压测试来说, 短路是绝缘非常严重的缺陷, 绝对不允许的. 然而, 我们经常将绝缘击穿与短路混淆. 那它们两者之间有何区别呢? 据试验表面, 绝缘击穿往往发生在电压施加过程中, 绝缘材料的电介质发生了变化, 而且造成施加电压的不稳定. 当电压超过了绝缘限制电流的临界点, 就会发生击穿的现象, 而且这种现象往往伴有瞬间闪络的情况发生. 而短路就是电源输出端直接导通;
( ?. j9 [* ?* g0 k( M  k第三, 在耐压测试时,如何判定绝缘击穿?
# b# \5 \" _7 v( Q+ K耐压测试的原理就是施加一高电压于绝缘上, 量测流经绝缘材料的电流值. 因此, 耐压测试是以漏电流值来判定产品的绝缘性能. 那么, 我们应该将漏电流设定为多少来判定产品的绝缘击穿呢? 在这里我们还需要了解2个概念----物理击穿&逻辑击穿. 物理击穿就是我们上面描述的定义, 而我们更多的情况以逻辑击穿来定义的, 就是在绝缘两端施加试验电压后, 流过绝缘的电流超过某个预定值; 我们通常以这个预定值(10mA, 100mA...)来判定产品绝缘是否"击穿".
作者: wwwabcd    时间: 2009-2-17 07:11
绝缘击穿是永久性破坏,不能恢复, 之后即使施加1/2 或更低试验电压,仍然会击穿
作者: alex.hu    时间: 2009-3-4 08:26
IEC60335-1中电流的设置标准中是有写100mA,但是有些耐压测试仪是没有办法设置到100mA的,那么这种情况下设置多少合适呢?另外美标里面只写出了电压值,电流值却没有写,哪位大哥能告诉我在标准上哪里有写啊,或者应该设置多少合适。谢谢!
作者: chunxiao9598    时间: 2009-3-16 08:40
请教一问题,电机的耐电压,1秒钟用多少伏的点?
作者: bay138668    时间: 2009-3-19 08:47
提示: 作者被禁止或删除 内容自动屏蔽
作者: victorlee    时间: 2009-3-19 10:48
我一般用泄漏电流来做确认产品是否击穿。耐压测试只是一个试测试。不过一般产品在耐压测试时漏电流(击穿电流)大于10MA,做泄漏电流是难以通过的。(我是做小家用电产品)
作者: kirk630330    时间: 2009-3-23 10:35
樓主分析的很詳細, 但是如果是IR 及Hi-pot之選擇, 我們該選擇那種為佳, 或是兩者皆測, 其判定又需依何規範, 謝謝解答
作者: peter1715    时间: 2009-3-26 23:54
一般耐压测试仪设为20mA,如果不能通过测试,就是设为100mA也不能通过测试,
作者: peach陶    时间: 2009-4-3 19:53
泄露电流和电气强度(耐压测试)虽然都是看电器产品的绝缘性能,但它们本质的区别是什么?
作者: yp963369    时间: 2009-4-8 14:14
我是做机械CE认证的,我知道EN 60204-1的测试标准,电气 设 备 的所有电路导线和保护接地电路之间应经受至少1s时间的耐压试验,打算工作在或低于PELV电压的电路除外。
7 I2 P2 `" t3 ^    试 验 电 压 应 :' L* V0 e$ q0 R2 E: e
    ----具 有 两倍的电气设备额定电源电压值或10 00V ,取其中的较大者;7 V7 y$ [& y- K
     ----频 率 为 50 H z或60H z;- i. W6 B0 v% ~- r% ?' t( Q
     ----由 最 小额定值为500V A的变压器供电。
0 Y$ _- s& a4 F" |, D& N     不适 宜 经受该试验的元件应在试验期间断开。
作者: shane    时间: 2009-4-11 12:52
耐压测试时的漏电流大多设置为5mA、10mA、100mA,不知道对不对呢?
作者: hiker    时间: 2009-4-14 23:27
标准中也没有具体要规定要设定多少毫安啊!我认为瞬间击穿的电流是无穷大的.所以要是你设定100mA打的过的话也算是符合要求的.
作者: xianallin    时间: 2009-4-15 09:25
我是做医疗器械安规检测的,应用IEC 60601-1/GB 9706.1-2007,耐压测试时,漏电流设置在10mA
作者: 珠江啤酒    时间: 2009-6-3 11:35
是否耐压测试的漏电流只是用来衡量设备是否击穿的阀值电流?
" `% S) s- ]3 b1 b8 d而泄露电流是EUT实际工作时的对地漏电流?
) f# F7 A+ ]$ i2 M" B' E5 z那就是说,如果耐压测试时的漏电流就不能用所谓的3.5mA来要求了?是吗?9 D( n, B9 Y, \; g4 s
我们只能要求泄露电流小于3.5mA。. r+ m7 g% d& _' F/ y8 y
请各位大老多多指教- o  p/ D( e& K* F3 A: ^; z
a.耐压时的电流 是你加的几KV后的电流。
3 `, |% D2 T0 n2 r: ?0 X. b漏电流是220V之类的额定电压下的泄露电流。$ x- _# S* ], A" }8 G/ }
高压通常是应用的在横跨被测试绝缘材料的二个部件之间, 譬如测试设备(EUT)的一次侧电路(Primary Circuit)和金属外壳。 如果绝缘材料在两个部件之间是足够的, 那么加在两个由绝缘体分离的导体之间的大电压只能产生非常小的电流流过绝缘体。 虽然这个小电流是可接受的, 但是空气绝缘或固体绝缘不应该发生击穿。% l  Y1 M. A/ N2 Z( k5 [9 O
  因此, 需要注意这个电流是因为局部放电或击穿的结果, 而不是由于电容联结引起的。
2 N& B$ X1 C* `1 G( f: Sb.泄漏电流(Leakage Current)命名为接触电流(Touch Current)。就是说,当一个人或者动物接触到设备的可接触部分的时候,流过人体或者动物体的电流。有另一个概念,就是“保护导体电流”,这相当于流过保护导体的电流。因此, 保护导体电流从来不是造成电击的原因, 因为依照定义, 保护导体一直被连接到大地。. d* W; Z/ p; \  T8 q/ i
    如果接触电流过大,那么操作者将会遭受电击,可能导致严重的伤害,这和人的体重有关系。通常的,超过1.0mA的电流流过人体,就能够造成电击伤害。伤害的严重性和电流的大小及人的体重有关。+ A: g, d! o7 j. a" C
c.楼主你说的3.5mA这个泄露电流,在60335中对应的产品是stationary class I motor-operated appliances。这个3.5mA是指泄露电流,泄露电流的意思就是在live parts 和accessible metal parts之间施加额定电压的1.06倍的电压所测得的电流值。当然还有一些小的要求在具体测试过程中。& d6 d+ h2 a! K
而耐压测试的意思是在live parts 和accessible metal parts之间施加上千伏的电压产生的漏电流,一般要求不超过30mA或100mA或200mA.耐压测试有三层含义,即electric strength test时间一般为60秒,routine test时间一般为3秒,inspection test时间一般为1秒。在IEC的标准里只有前两项。
作者: sgzcw    时间: 2009-6-13 09:14
对于GB4706.1-2005 13.3章的检验设备设定不是很明白。/ ~. j, g, k6 V8 _6 q
" P. o5 l+ p% }' j
我看仪器上有设定电压,时间,这些数据都比较明白的写在标准上,
9 C) g0 r- A5 c8 c! P/ ]8 o可是电流一项参数不是太懂,学习一下,4 S) S6 E2 a! G% N: D# J
不知道电流一项应该怎么设定?设定电流又是以什么标准为依据?
. D/ T! [$ @# I" ?2 qWHY??
: z4 ]7 P1 A# {9 w! M
作者: nw-interfans    时间: 2009-7-18 21:18
而IEC60884和VDE0620关于耐压实验是:/ p7 A4 `( m) Z* H* i. y
1:试验所用高压变压器应设计成:当将输出电压调到相应的试验电压后使输出接线端短路时,输出电流至少为200mA。
3 `5 z8 G/ _- b* p6 B注2:在输出电流小于100mA时,过电流继电器不得工作。
作者: 一叶知天下    时间: 2009-9-22 15:48
关于耐压测试有根据防护等级来测,但是对于整机来说,例如可以选择1250V  1min  也可以用1800V  3S  来测试 以此来评定其合格性,是单纯的节约时间 还是 另有公式计算。。。。请教
作者: ren8591    时间: 2009-10-4 07:33
小家电,GS搅拌机2500V /3.5mA/sec
" J( ~+ b2 U) l这些是怎么取的,好象没有这样的标准,
作者: figoxia    时间: 2009-10-6 16:59
这个问题讨论了很久了,看来还没有公认的最好的结果。 . N" g6 R2 v  ?( n$ y( b5 t
如果客人没有特别要求的话,个人认为IEC60335-1的附录A可以用。对 " w; M. {$ u# i8 C2 _" R- L' }: a* s. w
                                              0类,0I类,I类,II类                                                  III类 % `$ ?; M5 F0 ^
                                         <=150V                             >150V
! A) X3 D  k7 j4 r- |仅使用基本绝缘          800V/5mA/1S                    1000V/5mA/1S                    400V/5mA/S & Z1 h& Q) y1 e0 W3 |5 D7 h
用双重或加强绝缘       2000/5mA/1S                    2500V/5mA/1S                        --------- 7 m. r" b! M9 ^4 x
5 R# |1 V/ B9 Z
如果这个还不放心的话,电压可要其基础上上调1.2倍。 / C! v* D5 N$ c" H# u
对于高漏电流器具,取30mA.
1 w* U' ^! f/ H  P" f) S: B如果客人特别要求的话,就按客人要求做。我碰到过一个客人,要求我们3750V/0.2mA/1S的,变态的很,只要环境湿度稍微大一些,就fail了。当时郁闷的要死,最后死活要求客人改成1mA才OK。
作者: jwei    时间: 2010-7-15 11:21
英文版的看不懂,能否提供中文翻译版的
作者: 漫步云端    时间: 2010-7-22 13:57
引用第21楼nw-interfans于2009-12-28 21:18发表的  :. c- r$ a' ]' y- S9 J. b3 [
而IEC60884和VDE0620关于耐压实验是:7 a" y0 N- X2 R( k
1:试验所用高压变压器应设计成:当将输出电压调到相应的试验电压后使输出接线端短路时,输出电流至少为200mA。* ~  D9 q0 t* z7 K
注2:在输出电流小于100mA时,过电流继电器不得工作。
. A1 I6 H# l8 X- \, {1 I
60065标准中也有这么讲:
( Z" X9 j; D7 V1 b, [1 a+ g) v. ?, L8 H! P) x! d: l: n# S1 i1 X6 \* `7 Y
   The test voltages shall be obtained from a suitable source so designed that, when the output
5 K' Z5 V8 ~" j2 \2 m* j. O' LTERMINALS are short-circuited after the test voltage has been adjusted to the appropriate level,
3 \9 \/ S, |* x. D2 @the output current is at least 200 mA.; F: }# f  g+ z# u: I2 r; i' w
     An over-current device shall not trip when the output current is less than 100 mA.
" U/ \) m/ e) M6 X* k& m* n     Care shall be taken that the value of the test voltage applied is measured within ±3 %., {7 v' a  _' V- f  A
     Initially, not more than half of the prescribed test voltage is applied, then it is raised rapidly to
, {! d- @8 g1 \3 Y# C7 Dthe full value which is held for 1 min.
作者: bingshui918    时间: 2010-7-25 20:29
solid insulation in the relevant product standards, or even missing standards, this standard is applicable.
作者: andy82    时间: 2010-7-27 15:07
看了,感觉不是很明白,能否说明清楚一点?谢谢!
作者: solarhero    时间: 2010-11-11 13:00
学习了" z3 t5 `9 }8 I4 S- S% |6 J, A
受益中
作者: 飞鸽0553    时间: 2010-11-30 16:47
受教了 谢谢
作者: 安规007    时间: 2010-11-30 17:10
引用第3楼lixuf1于2008-12-22 20:29发表的  :2 a9 p+ t% m+ y* h$ k! \
当人体流过100mA以上电流时,人就会呼吸困难,心脏停跳

- Q/ p6 S8 N  H) k- j* C  S) s5 k呵呵,不会吧,难道是超人?通过这么大电流才会呼吸困难心脏停跳啊。
作者: stey    时间: 2010-12-2 10:57
电流设置越小越严格,0.2mA是个很苛刻严格的要求。很容易测试不通过,标准要求耐压仪有500VA的容量,没有规定电流,所以才造成测试时用的电流都不同。
作者: wangfeng123k    时间: 2011-2-21 10:47
一般产品,漏电流多大为合格
作者: endurance    时间: 2011-3-22 20:58
引用第31楼安规007于2010-11-30 17:10发表的  :7 T2 b5 E: v" o* _
' r- U6 H% w. U: ^

& G: N# W) m- ]9 B) G9 b呵呵,不会吧,难道是超人?通过这么大电流才会呼吸困难心脏停跳啊。
% J+ Z; D/ `9 |  X8 H2 Q
0 X  y( @3 J4 F; K/ J
; V5 x9 I* @; U
我觉得有道理,100MA人早就OVER了,
7 l0 a3 G/ Z+ Q3 `3 g% G30mA一般足以致人于危险了。
作者: Jelly05    时间: 2015-11-14 12:47
chunxiao9598 发表于 2009-3-16 08:40
& C7 y% ]" e/ w# T7 Q* n5 Z0 j请教一问题,电机的耐电压,1秒钟用多少伏的点?
" P# Y$ R& W" u
GB 12350中的20.2.3中规定用我们打60s的电压值的1.2倍即可




欢迎光临 安规网 (http://bbs1.angui.org/) Powered by Discuz! X3.2