' A1 f$ n9 f& f6 \我看了UL758沒看到此要求,才請教各位的作者: fasten 时间: 2012-5-24 17:36
你可以参考UL62: : q9 u3 K) v- k) l) I6 X9 Q4.1.9.1 Conductors shall be distinguished as follows:/ Z$ @, @) d0 g# ?$ v4 w; q
(a) Grounded (neutral) conductors shall be distinguished by one of the following methods, and9 z5 b" C4 v" g* z/ K
these colours shall be restricted to such use: 6 Y, P5 f3 S$ g(i) white or grey coloured braid;/ I V$ Q& ^! f' i" Q' u
(ii) white or grey coloured insulation; for jacketed cords furnished with appliances, one % W1 L! D' E7 ~$ k4 Fconductor may be light blue with the other conductors readily distinguishable from white 1 o8 v; o. l- Eor grey;# m) Y5 I5 h8 a, q2 Q
(iii) white or grey coloured separator in integral constructions only; $ M& p$ b/ T; T(iv) tinned conductor on integral constructions only; or . |) N" \" g! M+ o. W(v) one or more grooves, ridges, or white stripes on the exterior of integral 4 d! Z7 V, u5 h: g. x9 Xconstructions only. ( S: l- O) E& j; {/ s(b) Grounding conductors shall be distinguished by the colour green or a combination of the% S2 G7 W/ T% K2 _, Z
colours green and yellow. On a grounding conductor coloured green, one or more yellow stripes7 j% G+ Z% Q2 T0 b5 j
that cover no less than 5% and not more than 70% of the calculated circumference of the + _7 e7 V0 Q1 w5 \5 \2 z0 F+ ifinished conductor insulation shall be permitted.