xiaoning 发表于 2016-12-20 21:48

请教应急灯 AS-NZS-60598-2-22 的22.6.13怎么理解?

本帖最后由 xiaoning 于 2016-12-26 21:29 编辑

应急灯,澳洲标准的22.6.13:自容式应急灯不因短路,接地,中断而受影响,这里的短路指的是什么短路?是电池短路?接地指的是什么?中断指的是什么?要求通过22.12.7来验证,是指分别在短路,接地,中断 3个状态下进行0.9倍电压充电24小时后进行流明测试?用积分球还是分布式光度计?
22.6.13 The operation of a self-contained emergency luminaire in the emergency mode shall
not be influenced by a short-circuit, a contact to earth or an interruption, in the wiring of the
normal supply.
Compliance is checked by simulation of these supply wiring faults during the emergency mode
cycle of the test given in 22.12.7. The luminaire shall function normally during the test.

22.12.7 On completion of the thermal test (that is, having complete battery discharge
according to 22.12.4) a self-contained emergency luminaire shall be allowed to cool to its
rated ambient temperature (t
a
) or to 25 °C whichever is the higher and shall be subjected to a
24 h charging cycle at 0,9 times rated supply voltage after which the luminaire, with the lamp
as tested, shall operate satisfactorily in the emergency mode.provide the rated lumen output
at the end of the rated duration of operation.


xiaoning 发表于 2016-12-21 22:14

求指导,谢谢。

xiaoning 发表于 2016-12-24 19:53

求指导,谢谢,谢谢。

xiaoning 发表于 2016-12-25 12:08

求助,谢谢谢谢额谢谢谢谢谢谢

xiaoning 发表于 2016-12-27 22:07

这个问题到底是太难还是太简单呢?每人知道吗?
页: [1]
查看完整版本: 请教应急灯 AS-NZS-60598-2-22 的22.6.13怎么理解?